Safe Wattage
I want to buy a new air fryer. My present one consumes 1,500 watts. The new one would consume 1,800 watts. The breakers are rated for 20 amps and the the voltage is 120. Would it be safe using the 1,800 watts?
#2
Senior Member
Join Date: Feb 2008
Location: Peoria, IL
Posts: 4,275
Mentioned: 84 Post(s)
Tagged: 0 Thread(s)
Quoted: 1736 Post(s)
Liked 3,048 Times
in
1,446 Posts
Assuming that the breakers were selected because the wiring is rated for 20 amps, then you should be okay.
Might want to check that the plug and receptacle don't get warm, etc., but otherwise things seem alright.
Steve in Peoria
(why is this posted on BikeForums??)
Likes For steelbikeguy:
Likes For Bald Paul:
#4
Full Member
If the breakers are 20 Amps but the plugs are rated for 15 Amps you may be asking for trouble. 20 A circuits need to be wired with 12 ga. wire, 15 A get 14 ga. Breakers should (must?) match the capacity of the wire in the circuits they're supposed to be protecting after all. It's easy for the unwitting to use breakers that are over-capacity for the wiring in a given circuit unless They Know What They're Doing when they change breakers.
Plugs (receptacles are what they get plugged into) should be matched to the capacity of the circuit they're connected to:

The receptacle configurations highlighted in green in that chart are for 15A 125VAC-rated appliances, good for 1,800 watts.
The blue-highlighted configurations are for 20A 125VAC and should only be installed on circuits wired for 20A 120VAC service and protected with suitably-rated devices.
Circuits with those receptacles, of properly wired and protected, are fine for use with appliances of up to 2,400 watts.
(Common practice often has the plug's ground contact installed at the bottom so don't let that confuse you.)
Remember that total wattage of all appliances on a given circuit that are turned on and operating at the same time are what count.
Running a space heater (1,200 watts, maybe more) and a hair dryer (1,200 watts) at the same time on a single 15A 120VAC circuit will pop the breaker if it's wired properly.
(I grew up in a house wired with 2 - 15A 120VAC circuits. 2 story, 3 bedrooms, one bath... built after WWII. It was a frequent event somebody'd turn something on that's blow a fuse.)
2,400 watts 'demand' on a circuit that's wired for 1,800 watts max but protected with 2,400 watt (20A) breaker may cause a fire in the wiring from overcurrent.
Plugs (receptacles are what they get plugged into) should be matched to the capacity of the circuit they're connected to:

The receptacle configurations highlighted in green in that chart are for 15A 125VAC-rated appliances, good for 1,800 watts.
The blue-highlighted configurations are for 20A 125VAC and should only be installed on circuits wired for 20A 120VAC service and protected with suitably-rated devices.
Circuits with those receptacles, of properly wired and protected, are fine for use with appliances of up to 2,400 watts.
(Common practice often has the plug's ground contact installed at the bottom so don't let that confuse you.)
Remember that total wattage of all appliances on a given circuit that are turned on and operating at the same time are what count.
Running a space heater (1,200 watts, maybe more) and a hair dryer (1,200 watts) at the same time on a single 15A 120VAC circuit will pop the breaker if it's wired properly.
(I grew up in a house wired with 2 - 15A 120VAC circuits. 2 story, 3 bedrooms, one bath... built after WWII. It was a frequent event somebody'd turn something on that's blow a fuse.)
2,400 watts 'demand' on a circuit that's wired for 1,800 watts max but protected with 2,400 watt (20A) breaker may cause a fire in the wiring from overcurrent.
Last edited by spclark; 09-29-23 at 07:50 PM.
#5
Senior Member
Join Date: Aug 2010
Location: Madison, WI
Posts: 10,747
Bikes: 1961 Ideor, 1966 Perfekt 3 Speed AB Hub, 1994 Bridgestone MB-6, 2006 Airnimal Joey, 2009 Thorn Sherpa, 2013 Thorn Nomad MkII, 2015 VO Pass Hunter, 2017 Lynskey Backroad, 2017 Raleigh Gran Prix, 1980s Bianchi Mixte on a trainer. Others are now gone.
Mentioned: 45 Post(s)
Tagged: 0 Thread(s)
Quoted: 3249 Post(s)
Liked 1,313 Times
in
1,031 Posts
Likes For Tourist in MSN:
#6
Cantilever believer
Join Date: Nov 2021
Location: Phoenix, AZ
Posts: 1,244
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 410 Post(s)
Liked 1,366 Times
in
649 Posts
As I was wiring up the new high-capacity batteries on my Ridekick e-trailer with some serious 10-12 gauge, I was reminded of the old auto repair maxim:
"Any wire is a fusible link with sufficient current."
"Any wire is a fusible link with sufficient current."
__________________
Richard C. Moeur, PE - Phoenix AZ, USA
https://www.richardcmoeur.com/bikestuf.html
Richard C. Moeur, PE - Phoenix AZ, USA
https://www.richardcmoeur.com/bikestuf.html
Likes For daniell:
#8
I'm good to go!
Join Date: Jul 2017
Location: Mississippi
Posts: 14,146
Bikes: Tarmac Disc Comp Di2 - 2020
Mentioned: 48 Post(s)
Tagged: 0 Thread(s)
Quoted: 5838 Post(s)
Liked 4,456 Times
in
3,072 Posts
Watts divided by volts gives you the current draw or amperage. 1800/120 = 15. So on a circuit serviced by a 20 amp breaker you'll be good. If the outlet itself is rated for 15 amps, I wouldn't be too concerned. If it gets warm when being used then change it to 20 amps.
#9
Randomhead
Join Date: Aug 2008
Location: Happy Valley, Pennsylvania
Posts: 24,047
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 4 Post(s)
Liked 3,392 Times
in
2,324 Posts
All of the breakers in our house are 20 amps, the wiring is correct for 20 amps, and the outlets are all 15a. That probably gives a good estimate of the age of our house, because they could afford that wire.
Then they undid all of the benefits by backstabbing the outlets.
Then they undid all of the benefits by backstabbing the outlets.